View Full Version : Blown system fuse after voltage reg. replacement
dkees
December 10th, 2008, 04:34 PM
After determining that the voltage regulator was bad I ordered a replacement regulator from Ziller. When I replaced the regulator I was very careful to install the wiring to the new regulator in exactly the same way as the old one was wired. After installing the new regulator I fired up the generator using the manual start up. The generator started up and ran for a couple of seconds than shut down. No status lights or anything. After inspection I found that the 15 amp system fuse blew. I replaced the fuse in kind and started it up again and the fuse blew again.
Any Ideas?
dkees
December 10th, 2008, 04:38 PM
Sorry I forgot to include the following
Model 52500 16 kv
nat. gas
NYS SitePower Corp.
December 10th, 2008, 05:46 PM
Was it running fine before the VR swap out?
Check the VR wiring again. Here's the order for the connections on the VR (top down):
#11
#22
#4
#0
#6
#162
Look for pinched wires that may have happened during removal or re-installation.
dkees
December 10th, 2008, 09:42 PM
Update:
The third 15 amp fuse held, the generator fired up. I metered the output at 89 volts. three minutes later the engine shut off and I could not get it to restart.
dkees
December 10th, 2008, 09:44 PM
It was running fine before the swap out except for the fact that the output was 320 volts.
Kelly Myers
December 12th, 2008, 10:29 AM
Go review your wires plugged into the voltage regulator. Sounds like you might have a wire loose.
Here is how they should be:
11
22
4
0
6
162
dkees
December 12th, 2008, 04:17 PM
I checked the wiring and everything is as it should be. All terminal wire numbers check out with the schematics. . When I inspected the wiring the condition was as you would expect from a newer unit.
dkees
December 12th, 2008, 04:22 PM
The last wire is marked 2 not 162