Ira
August 22nd, 2008, 11:49 AM
Apologies for the long post, but I've got a "unique" setup...
Had a 5638 installed recently. Purchased from and installed by the local Guardian dealer. I'm confused by how the master electrician (from the dealer) configured the neutral/ground wires/bars/rods on my somewhat different setup.
My service entrance/meter is on the side of my "shop" building which is about 150 feet from my home. As it is now, the meter is on an outside wall, the ATS (RTSE200A3) is directly behind the meter on an inside wall, a load center (I will call it LC1) is immediately to the left of the ATS, and another load center (LC2) is immediately to the left of LC1. LC1 and LC2 have feed thru lugs, so power from LC1 goes to LC2, then goes underground to a load center (LC3) in my house. LC1 contains a main breaker for everything, as well as a few circuit breakers for my shop and water well pump. LC2 contains only a main breaker which allows me to turn off power from my shop to my house easily from my shop. LC3 (in my house) also has a main breaker.
The generator is located about 15 feet from the ATS, outside my shop.
There is a ground rod next to the generator. I didn't pull the generator cover to get all the details, but there is a ground wire connecting the generator frame to the ground rod.
There is a ground wire going from the ground bar in the ATS to the generator. I assume it is indirectly connected to the ground rod at the generator, also. The neutral bar in the ATS is bonded to the ATS enclosure. The neutral bar contains neutrals from the POCO and the generator and a neutral going to LC1.
LC1 contains both a neutral bar and a ground bar. Both are bonded to the enclosure. A neutral wire from the ATS is connected to the neutral bar, as are all of the neutrals from the shop circuits. The ground bar in LC1 contains a ground wire going to a ground rod just outside the shop (not the one next to the generator), and all of the ground wires from the shop circuits. There are wires on the two hot and one neutral feedthru lugs going from LC1 to LC2.
LC2 -- wires coming from the feedthru lugs in LC1 go to the main breaker lugs and neutral bar in LC2. Wires from the feedthru lugs in LC2 go underground to LC3 in the house. The neutral bar and ground bar are both bonded to the enclosure. There are two (?) ground wires going from the ground bar in LC2 to the same ground rod used by LC1. No other breakers in this box. Here's one of the oddities -- the ground wire going underground from LC2 to LC3 in the house is connected to the neutral bar in LC2.
LC3 (in the house) -- separate ground bar and neutral bar. Ground bar is bonded to the enclosure. Neutral bar is not bonded. All circuit grounds attached to the ground bar. All circuit neutrals attached to the unbonded neutral bar. The electrician did not make any changes to LC3. All of his work was done on the generator, ATS, LC1, and LC2.
I was always under the impression that neutrals and grounds should be isolated all the way back to the main service entrance (the ATS in this case). In other words, the neutral bars in LC1, LC2, and LC3 should be unbonded, and the ground/neutral circuit wires should be attached to their corresponding bars. That's how it was wired prior to the generator/ATS installation. Also, that the only ground wire connected to a ground rod should come from the main service entrance (the ATS), although adding a generator to the mix may change that.
When I discussed my concerns with the master electrician, he simply told me that everything would be done to code. Problem is that I live in an unincorporated area, so there are no electrical inspectors to check out the installation.
Is what the master electrician did correct?
Thanks,
Ira
Had a 5638 installed recently. Purchased from and installed by the local Guardian dealer. I'm confused by how the master electrician (from the dealer) configured the neutral/ground wires/bars/rods on my somewhat different setup.
My service entrance/meter is on the side of my "shop" building which is about 150 feet from my home. As it is now, the meter is on an outside wall, the ATS (RTSE200A3) is directly behind the meter on an inside wall, a load center (I will call it LC1) is immediately to the left of the ATS, and another load center (LC2) is immediately to the left of LC1. LC1 and LC2 have feed thru lugs, so power from LC1 goes to LC2, then goes underground to a load center (LC3) in my house. LC1 contains a main breaker for everything, as well as a few circuit breakers for my shop and water well pump. LC2 contains only a main breaker which allows me to turn off power from my shop to my house easily from my shop. LC3 (in my house) also has a main breaker.
The generator is located about 15 feet from the ATS, outside my shop.
There is a ground rod next to the generator. I didn't pull the generator cover to get all the details, but there is a ground wire connecting the generator frame to the ground rod.
There is a ground wire going from the ground bar in the ATS to the generator. I assume it is indirectly connected to the ground rod at the generator, also. The neutral bar in the ATS is bonded to the ATS enclosure. The neutral bar contains neutrals from the POCO and the generator and a neutral going to LC1.
LC1 contains both a neutral bar and a ground bar. Both are bonded to the enclosure. A neutral wire from the ATS is connected to the neutral bar, as are all of the neutrals from the shop circuits. The ground bar in LC1 contains a ground wire going to a ground rod just outside the shop (not the one next to the generator), and all of the ground wires from the shop circuits. There are wires on the two hot and one neutral feedthru lugs going from LC1 to LC2.
LC2 -- wires coming from the feedthru lugs in LC1 go to the main breaker lugs and neutral bar in LC2. Wires from the feedthru lugs in LC2 go underground to LC3 in the house. The neutral bar and ground bar are both bonded to the enclosure. There are two (?) ground wires going from the ground bar in LC2 to the same ground rod used by LC1. No other breakers in this box. Here's one of the oddities -- the ground wire going underground from LC2 to LC3 in the house is connected to the neutral bar in LC2.
LC3 (in the house) -- separate ground bar and neutral bar. Ground bar is bonded to the enclosure. Neutral bar is not bonded. All circuit grounds attached to the ground bar. All circuit neutrals attached to the unbonded neutral bar. The electrician did not make any changes to LC3. All of his work was done on the generator, ATS, LC1, and LC2.
I was always under the impression that neutrals and grounds should be isolated all the way back to the main service entrance (the ATS in this case). In other words, the neutral bars in LC1, LC2, and LC3 should be unbonded, and the ground/neutral circuit wires should be attached to their corresponding bars. That's how it was wired prior to the generator/ATS installation. Also, that the only ground wire connected to a ground rod should come from the main service entrance (the ATS), although adding a generator to the mix may change that.
When I discussed my concerns with the master electrician, he simply told me that everything would be done to code. Problem is that I live in an unincorporated area, so there are no electrical inspectors to check out the installation.
Is what the master electrician did correct?
Thanks,
Ira